    Hi…as per my knowledge hase angle control varies the effective voltage by connecting the
    load to the line only during some fraction of each half cycle,
    starting at an adjustable point in each half cycle, and ending at the
    next current zero crossing.Burst control varies the effective average voltage (over a longer
    time) by connecting the load to an integer number of complete half
    cycles in a burst, and then disconnecting the load from the line for
    some other integer number of full half cycles. Some systems use
    integer full cycles, rather than full half cycles, to prevent any net
    DC in the burst waveform. Burst mode has more low frequency ripple
    than phase control, but makes less radio frequency and harmonic noise,
    because all on switching is done very near the zero voltage points in
    the line voltage wave and all switch off points are at zero current
    points in the load current wave.